SLB: 5.0.5b (20230917)
  • Version 20230917
  • Updated default A-axis step/mm to match typical Vortex setups using 32nd microstepping
  • Updated defaults to accommodate some machine setups that couldn’t handle the max speeds and accelerations of the SLB
  • Changed min spindle speed, spindle on delay, and default enabled spindles to match typical spindle setups using the SLB
SLB-EXT: Main_grblHAL (20260525)
  • Version 20260525
  • Newest, main version of grblHAL
  • Requires gSender 1.6.2 or newer
  • Huanyang or generic ‘MODVFD’ spindle setups included
  • Read more about the use of the ‘MODVFD’ spindle profile for generic VFDs here.
Past Versions:
  • Main_grblHAL (20260318): default for SLB-EXT May 2026 ➜ June 2026
  • 5.0.11: default for SLB-EXT Oct 2024 ➜ April 2026
  • 5.0.5: default for SLB June ➜ Oct 2024
    • Updated default homing speed to stop occasional disconnection issues
    • Fixed E-stop hit requiring board power cycle to clear
  • 5.0.3: SLB firmware on original batch of 500 SLBs (April 2024)
Flashing Summary
To successfully flash new firmware onto your SLB, you’ll need:
  1. The firmware file (.hex file)
  2. A computer that can run gSender 1.6.2 or above, connected to the SLB/SLB-EXT controller over USB
    • The controller cannot flash through Ethernet
  3. For Windows, STM32Cube, downloaded and installed to your computer
  4. To note down any firmware settings that you have changed from the default firmware settings. This is especially important if you have a third-party CNC.
  5. To keep your SLB/SLB-EXT powered ON during flashing.
  6. To turn OFF any accessories that receive a control signal from the SLB, just in case the flashing process inadvertently sends control signals to those accessories.
  7. To unplug your VFD cable at the spindle side, not the VFD side.
The video shows the complete firmware update process, for an SLB-EXT on a Windows computer, using gSender to flash.
gSender Flashing
Current
  1. Connect to gSender over USB with the power on, and ensure the firmware is ‘grblHAL‘ not ‘grbl‘
  2. Go to the Config tab and click the Flash button
  3. Select the same COM port as before, and select grblHAL as your controller type.
  4. Click ‘Choose File’ to select the “.hex” firmware file you plan to update to.
  5. Click ‘Yes’ to begin the flashing process. If it stops before 100% and you see an error for:
  6. Once you see the loading bar at 100%, flashing is complete. Close the window and turn OFF and ON the SLB/SLB-EXT.
  7. Reconnect to gSender. Go to the Console tab and send the command $rst=$ to revert your machine back to the default firmware settings (you shouldn’t get any errors when you send this command).
  8. Power OFF and ON the controller.
  9. Select your machine profile and restore your defaults.
  10. Finally, if you had any specific settings from your previous setup that you want to reapply, connect back to gSender, go to Config and change those firmware values back.
    When finished, remember to press Apply New Settings, then turn OFF/ON the controller. If the settings aren't applying, make sure the controller is in an 'Idle' state, cleared of all Alarms, then try turning the controller OFF/ON again.
  11. Go to the ‘Console’, type in $i and press Run. Scroll up and check that the version number matches the firmware version you uploaded.
Congrats are in order, well done on successfully flashing the firmware!
Classic gSender
  1. Be connected to your SLB over USB with the power on, ensure the firmware selected is ‘grblHAL’ not ‘grbl’
  2. Go to the ‘Firmware’ tool and click the ‘Flash grblHAL’ button
  3. Ensure the COM port is correct (matches the board you’re connected to)
  4. Click ‘Choose File’ to select the “.hex” firmware file you plan to update to, in the picture below it’s the 5.0.7 firmware
  6. Once you see the loading bar at 100%, flashing is complete. Exit out of the firmware window and switch off the board with the power switch at the back then turn it back on again.
  7. Once it’s back on, you should be able to re-connect to it in gSender. Go to the ‘Console’ tab and send the command $rst=$ to revert your machine back to the default firmware settings (you shouldn’t get any errors when you send this command).
  8. Finally, if you had any specific settings from your previous setup that you want to reapply, connect back to gSender, go to Config and change those firmware values back.
  9. Go to the ‘Console’ and type in $i command and press Run. Scroll up and check that the version number matches the firmware version you uploaded.
STM Cube Flashing (Advanced)
STM Cube Flashing
Download the software from here (this is version 2.15.0) or for another OS go to STM’s website.
  1. On the SLB, switch off the power toggle switch at the black of the board or unplug it from power
  2. Use a jumper or metal tipped tool like a screwdriver or Allen key to short the BOOT pin (shown) and hold it in place
  3. Now turn the SLBs power toggle switch back on or reconnect power. You should see that most LEDs on the board are turned off now, especially the main Status LED.
  4. You can remove or let go of the BOOT jumper now.
  5. With the STM32 Cube Programmer opened on your computer:
    1. Select ‘USB’ in the blue drop down box at the top of the right of the window
    2. Click the refresh button next to ‘Port’, the board will typically show up as “USB1”
    3. If the board shows up, press the green ‘Connect’ button. If you still see “No DFU”, check your setup then click the refresh button again
    4. Go to the ‘Erasing & Programming’ tab on the left side of the screen
    5. Select the blue ‘Browse’ button to select the latest hex file (firmware file) on your computer
    6. Press the blue ‘Start Programming’ button
  6. Once complete, you’ll have to exit out of a bunch of small windows
  7. Switch off the board power switch then turn back on again, then reconnect to the board in gSender, ioSender, or any other g-code sender.
  8. Follow the same last 2 steps (7 and 8) of the gSender Flashing process and you should be done!
Troubleshooting
Windows Driver Update
If you’re failing to update your SLBs firmware and see the message “Error: LIBUSB_ERROR_NOT_SUPPORTED“, this stems from the sometimes problematic way that Windows handles USB devices. This isn’t a problem for Linux or Mac systems, but if your Windows computer is having this issue it can still be fixed by overriding the wrong driver it’s using with the correct one.
To do this we’ll use a program called Zadig. The program is only needed to make the fix, which should permanently fix SLB flashing issues:
  1. Download Zadig at https://zadig.akeo.ie/# (there’s an alternate download here).
  2. Put the SLB into DFU mode. There is two methods for this:
    • Connect to the SLB in gSender and type $dfu in the Console tab. This will disconnect it from gSender and it will no longer appear in the dropdown connection area. This step needs to happen successfully, if you get an error, assess your setup and do not move on to the next step.
    • Or use a jumper, flathead screwdriver, or other small piece of metal to short between two pins on the SLB near the USB port. The two pins will have “SPIN” written near them, and you’ll need to be shorting them while you use the power toggle switch to turn the SLB on.
  3. Open Zadig and in the toolbar click ‘Options’ ➜ ‘List all Devices’
  4. In the main dropdown, find and select the “STM32 Bootloader” device. This name might change depending on your current operating system.
  5. Make sure that “WinUSB” is the selected driver type.
  6. Click the “Replace Driver” button and wait for the operation to complete (if you happen to accidentally delete other drivers in the process, restarting your computer should bring them back).
  7. Power cycle the board to exit DFU mode, then give flashing another shot. If you followed all the steps you should now be able to change and update your SLBs firmware!
Bad Driver Install
If you got the error message “Unable to find valid device using vendor ID and product ID” and you just fixed your Windows drivers then that means you made a mistake in the driver update steps. If you weren’t messing with drivers, then just ensure your SLB is getting into DFU mode by typing $dfu into a g-code sender console or using the pin short method shown in the STM Cube Flashing section.
To fix the Windows driver:
  1. Open ‘Device Manager‘ in your Windows start menu
  2. Look under the ‘Ports‘ or ‘Universal Serial Bus‘ headings for the SLB which should include “STM32” in the name
  3. Right-click ➜ Uninstall device, then power cycle the board
  4. Once powered back up and reconnected, the SLB should reappear looking more normal. With this done, you can try flashing again – or if Windows still didn’t install the correct driver then go through the Windows Driver Update again.
  5. If this still doesn’t seem to work, you might’ve deleted the standard STM driver while using Zadig since the SLB wasn’t in DFU mode. In this case go to STMs website to re-download the drivers (they should work even though they say they’re for Windows 7) then try flashing again.
Ubuntu Driver Update
To set up udev rules to give your user account access to the SLB on Linux, follow these steps:
  1. Plug in your SLB
  2. Open a terminal and list all connected USB devices with lsusb
  3. Note the vendor ID and product ID. In the example, 1234 is the vendor ID and 5678 is the product ID.
    Bus 001 Device 002: ID 1234:5678 Sample USB Device
  4. Create a new udev rule file in the /etc/udev/rules.d/ directory; we’ll name it slb.rules:
    sudo nano /etc/udev/rules.d/slb.rules
  5. Add the following line to the file, replacing 1234 with the vendor ID and 5678 with the product ID:
    SUBSYSTEM=="usb", ATTR{idVendor}=="1234", ATTR{idProduct}=="5678", MODE="0660", GROUP="plugdev"
  6. Now add your user to the new plugdev group:
    sudo usermod -aG plugdev $USER
  7. Log out and log back in to apply the group changes.
  8. Reload the udev rules to apply the remaining changes:
    sudo udevadm control --reload-rules
    sudo udevadm trigger
  9. Finally, unplug and re-plug your SLB then check the device permissions have been set correctly (the exact path may vary according to your system):
    ls -l /dev/bus/usb/001/002
  10. You may also need to issue sudo chmod -R 777 /dev/bus/usb/
After completing these steps, you should have access to the SLB without needing sudo. If you still encounter issues, make sure that no other kernel drivers are conflicting with the device access. If everything is looking good, then go back up to continue Firmware flashing with gSender.
SLB Settings Descriptions
If you’d like to know all the ins and outs of the SLB’s firmware, and broader settings of grblHAL as a whole, you’ll find it all in the tables below.
For added clarity, settings that are currently unused on the SLB have been highlighted in orange. Also, the ones highlighted in blue though they are supported we don’t advise changing or are still building up documentation on.
$ Name Value (number) Units Description How to Use
$0 Step pulse time 5 microseconds Sets time length per step. Minimum 2 microseconds.
This needs to be reduced from the default value of 10 when max. step rates exceed approximately 80 kHz.
$1 Step idle delay 254 milliseconds Sets a short hold delay when stopping to let dynamics settle before disabling steppers. Value 255 keeps motors enabled.
$2 Step pulse invert X: OFF
Y: OFF
Z: OFF
A: OFF
(0)
Inverts the step signals (active low).
$3 Step direction invert X: OFF
Y: ON
Z: ON
A: OFF
(6)
Inverts the direction signals (active low).
$4 Invert stepper enable pin(s) X: ON
Y: ON
Z: ON
A: ON
(15)
Inverts the stepper driver enable signals. Most drivers uses active low enable requiring inversion.
NOTE: If the stepper drivers shares the same enable signal only X is used.
$5 Invert limit pins X: ON
Y: ON
Z: ON
A: ON
(15)
Inverts the axis limit input signals.
$6 Invert probe pin Enabled (1) Inverts the probe input pin signal.
$8 Ganged axes direction invert Disabled (0) Inverts the direction signals for the second motor used for ganged axes.
NOTE: This inversion will be applied in addition to the inversion from setting $3.
$9 PWM Spindle Enable: ON
RPM controls spindle en signal: OFF
(1)
Enable: Controls PWM output availability.
RPM controls spindle enable signal: When M3 or M4 is active,  S > 0 turns on spindle enable and S0 turns it off.
$10 Status report options Position in machine coords: ON
Buffer state: ON
Line numbers: ON
Feed & speed: ON
Pin state: ON
Work coord offset: ON
Overrides: ON
Probe coords: ON
Buffer sync on WCO change: ON
Parser state: OFF
Alarm substatus: OFF
Run substatus: OFF
(511)
Specifies optional data included in status reports. If Run substatus is enabled it may be used for simple probe protection.
NOTE: Parser state will be sent separately after the status report and only on changes.
$11 Junction deviation 0.010 mm Sets how fast Grbl travels through consecutive motions. Lower value slows it down.
$12 Arc tolerance 0.002 mm Sets the G2 and G3 arc tracing accuracy based on radial error. Beware: A very small value may effect performance.
$13 Report in inches Disabled (0) Enables inch units when returning any position and rate value that is not a settings value.
$14 Invert control pins Reset: OFF
Feed hold: ON
Cycle start: ON
Safety door: ON
EStop: OFF
(14)
Inverts the control signals (active low).
NOTE: Block delete, Optional stop, EStop and Probe connected are optional signals, availability is driver dependent.
$15 Invert coolant pins Flood: OFF
Mist: OFF
(0)
Inverts the coolant and mist signals (active low).
$16 Invert spindle signals Spindle en: OFF
Spindle dir: OFF
PWM: OFF
(0)
Inverts the spindle on, counterclockwise and PWM signals (active low).
NOTE: A hard reset of the controller is required after changing this setting.
$17 Pullup disable control pins Reset: OFF
Feed hold: OFF
Cycle start: OFF
Safety door: OFF
EStop: OFF
(0)
Disable the control signals pullup resistors. Potentially enables pulldown resistor if available.
NOTE: Block delete, Optional stop and EStop are optional signals, availability is driver dependent.
$18 Pullup disable limit pins X: OFF
Y: OFF
Z: OFF
A: OFF
(0)
Disable the limit signals pullup resistors. Potentially enables pulldown resistor if available.
$19 Pullup disable probe pin Disabled (0) Disable the probe signal pullup resistor. Potentially enables pulldown resistor if available.
$20 Soft limits enable Disabled (0) Enables soft limits checks within machine travel and sets alarm when exceeded. Requires homing. Docs
$21 Hard limits enable Enable: OFF
Strict mode: OFF
(0)
When enabled immediately halts motion and throws an alarm when a limit switch is triggered. In strict mode only homing is possible when a switch is engaged.
$22 Homing cycle Enable: OFF
Single axis commands: OFF
Homing on startup: OFF
Set machine origin: OFF
Two switches share one input: OFF
Allow manual: OFF
Override locks: OFF
Keep homed status on reset: OFF
(0)
Enables homing cycle. Requires limit switches on axes to be automatically homed.
When `Enable single axis commands` is checked, single axis homing can be performed by $H<axis letter> commands.
When `Allow manual` is checked, axes not homed automatically may be homed manually by $H or $H<axis letter> commands.
`Override locks` is for allowing a soft reset to disable `Homing on startup required`.
$23 Homing direction invert X: ON
Y: ON
Z: OFF
A: ON
(11)
Homing searches for a switch in the positive direction. Set axis bit to search in negative direction.
$24 Homing locate feed rate 150 mm/min Feed rate to slowly engage limit switch to determine its location accurately.
$25 Homing search seek rate 4300 mm/min Seek rate to quickly find the limit switch before the slower locating phase.
$26 Homing switch debounce delay 25 milliseconds Sets a short delay between phases of homing cycle to let a switch debounce.
$27 Homing switch pull-off distance 1.5 mm Retract distance after triggering switch to disengage it. Homing will fail if switch isn’t cleared.
$28 G73 retract distance 0.1 mm G73 retract distance (for chip breaking drilling).
$29 Pulse delay 0 microseconds Step pulse delay.
Normally leave this at 0 as there is an implicit delay on direction changes when AMASS is active.
$30 Maximum spindle speed 24000 RPM Maximum spindle speed, can be overridden by spindle plugins. Docs
$31 Minimum spindle speed 7500 RPM Minimum spindle speed, can be overridden by spindle plugins.
$32 Mode of operation Normal
(0)
Laser mode: consecutive G1/2/3 commands will not halt when spindle speed is changed.
Lathe mode: allows use of G7, G8, G96 and G97.
$33 Spindle PWM frequency 1000 Hz Spindle PWM frequency.
$34 Spindle PWM off value 0 percent Spindle PWM off value in percent (duty cycle).
$35 Spindle PWM min value 0 percent Spindle PWM min value in percent (duty cycle).
$36 Spindle PWM max value 100 percent Spindle PWM max value in percent (duty cycle).
$37 Steppers de-energize X: OFF
Y: OFF
Z: OFF
A: OFF
(0)
Specifies which steppers not to disable when stopped. Docs
$39 Enable legacy RT commands Enabled (1) Enables “normal” processing of ?, ! and ~ characters when part of $-setting or comment. If disabled then they are added to the input string instead.
$40 Limit jog commands Enabled (1) Limit jog commands to machine limits for homed axes. Docs
$41 Parking cycle Enable: ON
Parking override control: OFF
Deactivate upon init: OFF
(1)
Enables parking cycle, requires parking axis homed.
$42 Parking axis Z
(2)
Define which axis that performs the parking motion.
$43 Homing passes 1 Number of homing passes. Minimum 1, maximum 128.
$44 Axes homing, first pass X: OFF
Y: OFF
Z: ON
A: OFF
(4)
Axes to home in first pass.
$45 Axes homing, second pass X: ON
Y: ON
Z: OFF
A: OFF
(3)
Axes to home in second pass.
$46 Axes homing, third pass X: OFF
Y: OFF
Z: OFF
A: OFF
(0)
Axes to home in third pass.
$47 Axes homing, fourth pass X: OFF
Y: OFF
Z: OFF
A: OFF
(0)
Axes to home in fourth pass.
$56 Parking pull-out distance 5 mm Spindle pull-out and plunge distance in mm.Incremental distance.
$57 Parking pull-out rate 100 mm/min Spindle pull-out/plunge slow feed rate in mm/min.
$58 Parking target -5 mm Parking axis target. In mm, as machine coordinate [-max_travel, 0].
$59 Parking fast rate 500 mm/min Parking fast rate to target after pull-out in mm/min.
$60 Restore overrides Enabled (1) Restore overrides to default values at program end.
$61 Safety door options Ignore when idle: ON
Keep coolant state: ON
(3)
Enable this if it is desirable to open the safety door when in IDLE mode (eg. for jogging).
$62 Sleep enable Disabled (0) Enable sleep mode.
$63 Feed hold actions Disable laser: ON
Restore spindle and coolant state: ON
(3)
Actions taken during feed hold and on resume from feed hold.
$64 Force init alarm Disabled (0) Starts Grbl in alarm mode after a cold reset.
$65 Probing feed override Disabled (0) Allow feed override during probing.
$70 Network services Telnet: ON
Websocket: ON
FTP: ON
(11)
Network services/protocols to enable.
Docs
$100 X-axis travel resolution 800 step/mm Travel resolution in steps per millimeter.
$101 Y-axis travel resolution 800 step/mm
$102 Z-axis travel resolution 800 step/mm
$103 A-axis travel resolution 79.012345679 step/deg
$110 X-axis maximum rate 4000 mm/min Maximum rate. Used as G0 rapid rate. Docs
$111 Y-axis maximum rate 4000 mm/min
$112 Z-axis maximum rate 4000 mm/min
$113 A-axis maximum rate 8000 deg/min
$120 X-axis acceleration 750 mm/sec^2 Acceleration. Used for motion planning to not exceed motor torque and lose steps.
$121 Y-axis acceleration 750 mm/sec^2
$122 Z-axis acceleration 750 mm/sec^2
$123 A-axis acceleration 1000 deg/sec^2
$130 X-axis maximum travel 810 mm Maximum axis travel distance from homing switch. Determines valid machine space for soft-limits and homing search distances.
$131 Y-axis maximum travel 855 mm
$132 Z-axis maximum travel 120 mm
$133 A-axis maximum travel 0 deg
$140 X-axis motor current 2800 mA Motor current in mA (RMS).
NOTE: Only used for axes controlled by a Trinamic driver.
$141 Y-axis motor current
$142 Z-axis motor current
$143 A-axis motor current 0
$150 X-axis microsteps 32 steps Microsteps per fullstep.
$151 Y-axis microsteps
$152 Z-axis microsteps
$153 A-axis microsteps 16
$180 X-axis homing locate feed rate 150 mm/min Feed rate to slowly engage limit switch to determine its location accurately.
NOTE: Defaults to $24 setting if axis isn’t controlled by a Trinamic driver.
Docs
$181 Y-axis homing locate feed rate
$182 Z-axis homing locate feed rate
$183 A-axis homing locate feed rate
$190 X-axis homing search seek rate 4300 mm/min Seek rate to quickly find the limit switch before the slower locating phase.
NOTE: Defaults to $25 setting if axis isn’t controlled by a Trinamic driver.
Docs
$191 Y-axis homing search seek rate
$192 Z-axis homing search seek rate
$193 A-axis homing search seek rate
$200 X-axis StallGuard2 fast threshold 22 StallGuard threshold for fast (seek) homing phase.
$201 Y-axis StallGuard2 fast threshold
$202 Z-axis StallGuard2 fast threshold
$203 A-axis StallGuard2 fast threshold
$210 X-axis hold current 35 % Motor current at standstill as a percentage of full current.
NOTE: If grblHAL is configured to disable motors on standstill this setting has no use. Only used for axes controlled by a Trinamic driver.
Docs
$211 Y-axis hold current
$212 Z-axis hold current
$213 A-axis hold current 50
$220 X-axis stallGuard2 slow threshold 22 StallGuard threshold for slow (feed) homing phase.
$221 Y-axis stallGuard2 slow threshold
$222 Z-axis stallGuard2 slow threshold
$223 A-axis stallGuard2 slow threshold
$300 Hostname grblHAL Network hostname.
~Controller reset required for setting change to take effect~
Docs
$301 IP mode Static
(0)
IP mode.
$302 IP address 192.168.5.1 Static IP address.
$303 Gateway 192.168.5.1 Static gateway address.
$304 Netmask 255.255.255.0 Static netmask.
$305 Telnet port 23 (Raw) Telnet port number listening for incoming connections.
$307 Websocket port 80 Websocket port number listening for incoming connections.
NOTE: WebUI requires this to be HTTP port number + 1.
$308 FTP port 21 FTP port number listening for incoming connections.
$338 Trinamic driver X: ON
Y: ON
Z: ON
A: OFF
(7)
Enable SPI or UART controlled Trinamic drivers for axes.
$339 Sensorless homing X: OFF
Y: OFF
Z: OFF
A: OFF
(0)
Enable sensorless homing for axes. Requires SPI or UART controlled Trinamic drivers.
$340 Spindle at speed tolerance 0 percent Spindle at speed tolerance as percentage deviation from programmed speed, set to 0 to disable.
If not within tolerance when checked after spindle on delay ($392) alarm 14 is raised.
$341 Tool change mode Normal
(0)
Normal: allows jogging for manual touch off. Set new position manually.
Manual touch off: retracts tool axis to home position for tool change, use jogging or $TPW for touch off.
Manual touch off @ G59.3: retracts tool axis to home position then to G59.3 position for tool change, use jogging or $TPW for touch off.
Automatic touch off @ G59.3: retracts tool axis to home position for tool change, then to G59.3 position for automatic touch off.
All modes except “Normal” and “Ignore M6” returns the tool (controlled point) to original position after touch off.
$342 Tool change probing distance 30 mm Maximum probing distance for automatic or $TPW touch off.
$343 Tool change locate feed rate 25 mm/min Feed rate to slowly engage tool change sensor to determine the tool offset accurately.
$344 Tool change search seek rate 200 mm/min Seek rate to quickly find the tool change sensor before the slower locating phase.
$345 Tool change probe pull-off rate 200 mm/min Pull-off rate for the retract move before the slower locating phase.
$346 Restore position after M6 Enabled (1) When set the spindle is moved so that the controlled point (tool tip) is the same as before the M6 command, if not the spindle is only moved to the Z home position.
$370 Invert I/O Port inputs (0) Invert IOPort inputs.
$372 Invert I/O Port outputs (0) Invert IOPort output.
$374 Modbus baud rate 19200
(3)
$375 Modbus RX timeout 50 milliseconds
$376 Rotational axes A-Axis: ON
(1)
$384 Disable G92 persistence Disabled (0) Disables save/restore of G92 offset to non-volatile storage (NVS).
$392 Spindle on delay 11 s Delay to allow spindle to spin up after safety door is opened.
$393 Coolant on delay 1 s Delay to allow coolant to restart after safety door is opened.
$395 Default spindle SLB_SPINDLE
(0)
Spindle selected on startup.
$398 Planner buffer blocks 128 Number of blocks in the planner buffer.
$450 Button 1 action Cycle start
(1)
Assign a real-time action to button 1, or run your own macro g-code. Docs
$451 Button 2 action Pause
(2)
Assign a real-time action to button 2, or run your own macro g-code.
$452 Button 3 action Halt
(4)
Assign a real-time action to button 3, or run your own macro g-code.
$453 Button 1 macro G4P0 Macro content, limited to 127 characters. Separate lines with the vertical bar character |.
$454 Button 2 macro G4P0 Macro content, limited to 127 characters. Separate lines with the vertical bar character |.
$455 Button 3 macro G4P0 Macro content, limited to 127 characters. Separate lines with the vertical bar character |.
$456 Aux output 0 trigger Spindle/Laser enable
(0)
A second, more common action can be assigned to trigger this output. M62/63 P# is always available as a buffered on/off or M64/65 P# as an immediate on/off. Docs
$457 Aux output 1 trigger Flood enable
(2)
$458 Aux output 2 trigger Spindle/Laser enable
(0)
$459 Aux output 3 trigger Flood enable
(2)
$462 Run/stop register 8192 decimal MODVFD register for run/stop. Docs
$463 Frequency set register 8193 decimal MODVFD register to set frequency.
$464 Frequency get register 8451 decimal MODVFD register to get frequency.
$465 Run CW command 18 decimal MODVFD command word for CW.
$466 Run CCW command 34 decimal MODVFD command word for CCW.
$467 Stop command 1 decimal MODVFD command word for stop.
$468 RPM input multiplier 50 MODVFD RPM value multiplier for programming RPM.
$469 RPM input divider 60 MODVFD RPM value divider for programming RPM.
$470 RPM output multiplier 60 MODVFD RPM value multiplier for reading RPM.
$471 RPM output divider 100 MODVFD RPM value divider for reading RPM.
$478 Spindle 2 Modbus address 3 Spindle 2 Modbus address.
$479 Spindle 3 Modbus address 4 Spindle 3 Modbus address.
$481 Autoreport interval 0 ms Interval the real time report will be sent, set to 0 to disable.
$484 Unlock required after E-stop Enabled (1) If set, unlock (by sending $X) is required after resetting a cleared E-Stop condition.
$486 Lock coordinate systems G59.1: OFF
G59.2: OFF
G59.3: OFF
(0)
Lock coordinate systems against accidental changes.
$511 Spindle 1 SLB_LASER
(7)
Spindle to use as spindle 1.
Docs
$512 Spindle 2 MODVFD
(5)
Spindle to use as spindle 2.
$513 Spindle 3 Disabled
(8)
Spindle to use as spindle 3.
$520 Spindle 0 tool number start 0 Start of tool numbers for selecting spindle 0 (default spindle). Normally leave this at 0.
$521 Spindle 1 tool number start 0 Start of tool numbers for selecting spindle 1.
$522 Spindle 2 tool number start 0 Start of tool numbers for selecting spindle 2.
$523 Spindle 3 tool number start 0 Start of tool numbers for selecting spindle 3.
$650 Chopper toff 1 Off time. Duration of slow decay phase as a multiple of system clock periods: NCLK= 24 + (32 x TOFF). This will limit the maximum chopper frequency (0-15).
0: MOSFETs shut off, driver disabled.
1: Use with TBL of minimum 24 clocks.
$651 Chopper tbl 1 Blanking time interval in system clock periods (0-3 = 16,24,36,54). Needs to cover the switching event and the duration of the ringing on the sense resistor.
$652 Chopper chm 0 Chopper mode. Affects HDEC, HEND, and HSTRT parameters.
0: Standard mode (SpreadCycle).
1: Constant TOFF with fast decay time. Fast decay is after on time. Fast decay time is also terminated when the negative nominal current is reached.
$653 Chopper hstr 2 CHM=0: Hysteresis start, offset from HEND (0-7 = 1-8). To be effective, HEND+HSTRT must be ≤15.
CHM=1: Fast decay time. Three least-significant bits of the duration of the fast decay phase. The MSB is HDEC0. Fast decay time is a multiple of system clock periods: NCLK= 32 x (HDEC0+HSTRT).
$654 Chopper hend 8 Can be either negative, zero, or positive, 0-15 = -3 to 12.
CHM=0: Hysteresis end (low). Sets the hysteresis end value after a number of decrements, used for the hysteresis chopper and controlled by HDEC. HSTRT+HEND must be less than 16. 1/512 adds to the current setting.
CHM=1: Sine wave offset. A positive offset corrects for zero crossing error. 1/512 adds to the absolute value of each sine wave entry.
$655 Chopper hdec 0 CHM=0: Hysteresis decrement interval period in system clock periods. Determines the slope of the hysteresis during on time from fast to very slow (0-3 = 16,32,48,64).
CHM=1: Fast decay mode.
$656 Chopper rndtf 1 Change from fixed to randomized TOFF times, by dNCLK= -24 to +6 clocks. Only for CHM=1.
$657 THRESH 22 StallGuard threshold.
$658 CoolStep semin 7 Lower CoolStep threshold. If the SG value falls below SEMIN x 32, the coil current scaling factor is increased (0-15).
0: CoolStep disabled.
$659 CoolStep seup 3 Number of increments of the coil current each time SG is sampled below the lower threshold (0-3 = 1,2,4,8).
$660 CoolStep semax 0 Upper CoolStep threshold offset from lower threshold. If SG is sampled above (SEMIN+SEMAX+1)x32 enough times, the coil current scaling factor is decremented (0-15).
$661 CoolStep sedn 3 Number of times SG must be sampled above the upper threshold before the coil current is decremented (0-3 = 32,8,2,1).
$662 CoolStep seimin 0 Minimum CoolStep current as a factor of the set motor current.
0: 1/2, 1: 1/4
$663 drvconf_reg 41759 DRVCONF register defaults 0xA31F. All protections enabled.
$664 Ring pixels 0 Number of individual pixels or LEDs connected.
Docs
$665 Rail pixels 1 Number of individual pixels or LEDs connected. Include the onboard LED.
$666 Using add-ons (0) Sienci specific capability flags.
$668 Invert TLS input Enabled (1) Invert the TLS input ahead of the OR function.
$730 Maximum laser power 255 Maximum S word power for laser. Docs
$731 Minimum laser power 0 Minimum S word power for laser.
$733 Laser PWM frequency 1000 Hz Laser PWM frequency.
$734 Laser PWM off value 0 percent Laser PWM off value in percent (duty cycle).
$735 Laser PWM min value 0 percent Laser PWM min value in percent (duty cycle).
$736 Laser PWM max value 100 percent Laser PWM max value in percent (duty cycle).
$741 Laser X offset 0 mm Laser offset from spindle on X-axis.
$742 Laser Y offset 0 mm Laser offset from spindle on Y-axis.
$743 Invert laser signals Enable: OFF
PWM: OFF
(0)