10. Spindle Kit Setup

image_print

Spindle and Controller Connections

The instructions below must be followed in the exact order they are presented, otherwise the controller won’t be able to communicate with the VFD and will present an ‘Alarm 14’ error.

If your SLB-EXT is powered on, please turn it OFF now.

Power switch on SLB-EXT

Ensure that the spindle cable connector is installed on top of the spindle.

Connecting spindle cable to spindle

Then check that the RS485 wire is plugged into the SLB-EXT controller.

Connecting RS485 to SLB-EXT

Ensure the RS485 cable is plugged into the connector above the OFF-ON switch and not the connector below the USB cable.

RS485 Correct Connector Location

Plug in the power cord from the VFD unit into a wall outlet or extension cord now. If you’re using an extension cord, ensure that it is rated for 1500W of power. The VFD must be ON before the SLB-EXT, otherwise they will not properly “greet” each other. 

Connecting spindle to power

The VFD screen should blink on with red text. Blinking text is normal behaviour for the VFD display.

Turn ON the controller using the power switch and make sure the E-stop is released. We will now move to setting things up on gSender.

Connect to gSender, as you did in the First Movements section.

gSender Settings

Open the dropdown menus below to see the correct setup steps for the gSender version you have.  

gSender 1.6.0 and above

gSender 1.6.0 and above

With your computer connected to your machine, and no alarms active, we’ll need to enable some settings to allow for communication between your controller and the spindle.

1. Go to Tools, then select Accessory Installation

2. Select Sienci Spindle. Then follow the instructions in the installation wizard to finish setting up your spindle.

3. Once you complete all the steps in the installation wizard, go back to the main page, Carve.

4. You should now see a ‘Spindle/Laser’ tab on the bottom right corner of gSender. Make sure H-100 is selected in the ‘Spindles’ dropdown.

5. Then, you can try setting a desired RPM speed, then click ‘Forward’ to have the spindle start spinning up to the set speed. Ensure there are no obstacles in the way of the spindle or any loose parts nearby before turning this on. In the event of any emergency, press the physical E-stop button to immediately stop the spindle.

gSender 1.5.0 to 1.5.9

gSender 1.5.0 to 1.5.9

With your computer connected to your machine, and no alarms active, we’ll need to enable some settings to allow for communication between your controller and the spindle.

1. In the Console at the bottom right corner, enter $i then press Run.

2. Check what Driver Version you have.

3. Press ‘Load File’ and select the file you just downloaded.

Then press ‘Start.’

4. Once the file is done, turn OFF the controller at the power switch.

5. Unplug the VFD spindle from power.

6. Close gSender.

7. Then, plug the VFD spindle back into power, turn ON the controller, and open gSender and reconnect.

8. Navigate to ‘Config’ then at the left header select ‘Spindle/Laser.’

9. Turn ON ‘Enable Spindle/Laser functionalities’ toggle (or ‘Spindle/Laser controls’ if you are on gSender 1.5.4 and higher).

 

10. Go back to the main page, Carve.

11. You should now see a ‘Spindle/Laser’ tab on the bottom right corner of gSender. Make sure H-100 is selected in the ‘Spindles’ dropdown.

12. Then, you can try setting a desired RPM speed, then click ‘Forward’ to have the spindle start spinning up to the set speed. Ensure there are no obstacles in the way of the spindle or any loose parts nearby before turning this on. In the event of any emergency, press the physical E-stop button to immediately stop the spindle.

gSender 1.4.12 and below

gSender 1.4.12 and below

1. With your computer connected to your machine, and no alarms active, we’ll need to enable some settings to allow for communication between your controller and the spindle. This can be done by downloading and running this file Sienci Spindle Configuration (SLB-EXT).

2. Press ‘Load Job’ and select the file you just downloaded.

3. Then press ‘Start.’

4. Once the file has finished, we will now reset everything so our changes can take effect. Turn OFF the controller at the power switch.

5. Unplug the spindle from power.

6. Close gSender.

7. Then, plug the spindle back into power, turn ON the controller, and open gSender and reconnect.

8. In gSender, click the small gear icon to open the settings menu, then select the ‘Spindle/Laser’ tab. Here, toggle the ‘Spindle/Laser’ option to enable this menu in gSender.

Toggling the spindle on

9. Set the spindle’s ‘Min’ and ‘Max’ speeds as 7500 and 24,000 RPM, respectively.

Correct AltMill spindle speed settings

10. You should now see a ‘Spindle/Laser’ tab on the bottom right corner of gSender. Make sure H-100 is selected in the ‘Spindles’ dropdown.

11. Then, you can try setting a desired RPM speed, then clicking ‘CW (M3)’ to have the spindle start spinning up to the set speed. Ensure there are no obstacles in the way of the spindle or any loose parts nearby before turning this on. In the event of any emergency, press the physical E-stop button to immediately stop the spindle.

Spindle Direction

While testing, make sure the spindle is spinning the correct direction by watching as the spindle slows down to a stop once done.

Direction of spindle 

If the spindle is spinning in the opposite direction, swap any of two wires on the U, V, W terminals. Warning, Electrical Hazard! Unplug the VFD from the power source and the controller before swapping the wires. 

Changing spindle direction using U, V wires

Spindle Break-in

The grease inside the bearings may have shifted during transportation, it is recommended that you run a “break-in” cycle to redistribute the grease before using your spindle. To do this, you can download and run the g-code file below on gSender, which should take 1 hour 40 minutes to run.

Sienci Spindle Break-in.gcode

To run the file connect to gSender and press ‘Load File’ at the bottom left corner. Select the file and you should see a ‘Start Job’ button appear, go ahead and click that.

For regular maintenance of your spindle, we recommend running a shorter “warm up” g-code.

Sienci Spindle Warm up.gcode

Finishing Up

Congratulations on completing spindle setup! This is one of the trickiest parts of getting the AltMill ready.

If you are done for the day, just turn off the SLB-EXT controller using the power toggle. You can leave the VFD plugged into wall power.

However, if you choose to unplug the VFD, please follow this precise order for starting up each time, to avoid alarms:

1. Make sure the controller is plugged into power but turned OFF
2. Plug spindle into power, the VFD should blink with red text
3. Then turn on the controller using the power toggle

If you have already set up your wasteboard, feel free to continue into the Final Checks article. Otherwise, to the Wasteboard we go!